A refrigerant leak in the evaporator shell of a system using R123 will likely result in what condition?

Prepare for the FDNY Respiratory Medical Officer Test. Engage with flashcards and multiple-choice questions, each with detailed hints and explanations. Start your successful exam preparation journey today!

A refrigerant leak in the evaporator shell of a system using R123 will likely lead to a higher than normal high side pressure condition. This occurs due to the imbalance created in the refrigerant cycle.

In a typical refrigeration cycle, the evaporator absorbs heat, allowing the refrigerant to evaporate and create a low-pressure environment. Meanwhile, the compressor moves the vaporized refrigerant from the low-pressure side (evaporator) to the high-pressure side where it can release heat and condense back to a liquid. When there is a leak in the evaporator shell, it interrupts the cooling process by allowing refrigerant to escape.

In this scenario, the compressor continues to function, trying to compensate for the refrigerant that is lost. As a result, it may not be able to properly manage the refrigerant flow, leading to excessive discharge pressure on the high side. This increased pressure occurs because the compressor is attempting to pull in vapor at a much greater rate to keep the balance, but the refrigerant that is meant to condense is escaping, causing the pressure to rise above normal levels.

This understanding of system behavior under a refrigerant leak illustrates why the condition described in the correct option is expected.